11/23/2015 2:29 PM | |
Joined: 7/30/2013 Last visit: 2/29/2024 Posts: 40 Rating: (0) |
Hi, I am troubleshooting a SIWAREX231 installation. CPU is 6ES7214-1AG40 For zeroing I am loading 1001 to s_CMD2.i_CMD_CODE and then setting s_CMD2.i_CMD_TRIGGER from the HMI. While I am getting s_CMD2.i_CMD_FinishedOK = True everytime zeroing isnt happeing every time. I have been looking at the manual for any clues and so far found nothing. How do I solve this? Thanks in advance I have attached siwarex configuration file for you reference. BR//Ashadul Attachmentsiwrex configuration.zip (180 Downloads) |
Last edited by: ashadul at: 11/23/2015 2:31:48 PM |
|
11/24/2015 10:22 AM | |
Posts: 206 Rating: (22) |
Hi Ashadul, shielding is always an issue that you must care fore.See FAQ: https://support.industry.siemens.com/cs/de/en/view/23923799 Also with the filter settings you can stabilize the weight value. With the FW you have there is an issue with the filters, you should update it to the actual one: https://support.industry.siemens.com/cs/de/en/view/75231231 you might also change the function blocks in your PLC program: https://support.industry.siemens.com/cs/ww/en/view/66825585
The Standstill bit depends on two parameters in DR3/"Additional Paramters" "Standstill range" and "Standstill time". With your settings "Standstill range" = 1d and "Standstill time" = 2000ms, the weight needs to be in a range of +/-10g(1d) during 2s to be detected as Standstill. See also the manual chapter 8.3.21 ff https://support.industry.siemens.com/cs/de/en/view/90229056 . Regards ABenno |
This contribution was helpful to1 thankful Users |
11/27/2015 7:51 AM | |
Joined: 7/30/2013 Last visit: 2/29/2024 Posts: 40 Rating: (0) |
Hi, What does it mean standstill range (in d)? Is in percentage of weight unit? BR//Ashaduk |