3/25/2010 6:30 AM | |
Posts: 691 Rating: (37) |
Dear hac_am2003
|
3/25/2010 7:47 AM | |
Joined: 10/7/2005 Last visit: 9/12/2024 Posts: 3020 Rating: (1054)
|
Hello hac_am2003 please check your "set PG/PC interface" setting (see Options menu in Simatic Manager). You problem could be as simple as it being set to MPI, but the MPI/DP port of your CPU isconfigured as a DP port (via the configuration on the MMC that you put into the CPU which would also neatly explain the BF LED). Anyway, try settignit to "PC Adapter (AUTO)"and see if this helps. |
Cheers |
|
3/25/2010 9:15 AM | |
Joined: 4/24/2006 Last visit: 9/12/2024 Posts: 8736 Rating: (1167) |
Dera hac_am2003, I guess you used the MMC in another CPU. I would advise you to reset the MMC in CPU 315-2PN/DP. Please have a look at this link: how do you reset a SIMATIC S7-300 CPU and MMC (default reset or overall reset)? follow the three steps, the mentioned times are important. And a step 4 would be: hold in MRES position for at least 5 seconds. Best regards, Wizard |
3/26/2010 9:28 AM | |
Joined: 4/24/2006 Last visit: 9/12/2024 Posts: 8736 Rating: (1167) |
Hi, When SF led is on, you will have to go to Diagnostic buffer to see what's wrong. Best regards, Wizard |