10/12/2018 5:01 AM | |
Joined: 10/7/2009 Last visit: 2/10/2025 Posts: 266 Rating:
|
Dear morylATCS, For the Basic Panels 2nd generation, the historical data only supports storage location: TXT file (Unicode) and Path: \USB_X60.1\ This link may give you some hints: Logging Process Values and Alarms with WinCC (TIA Portal) For Trend View, you can get help from the online help of TIA Portal, just move the mouse over the Trend view control in the toolbox and click the link appeared in the tooltip. Best regards, Yu-wen |
Last edited by: Jen_Moderator at: 10/16/2018 7:44:45 AMOptimized link. |
|
10/12/2018 7:57 AM | |
Posts: 39 Rating:
|
Dear Yu-wen Tang, thank you for answer I'm not sure if I understood your answer correctly, so I can't save any data on HMI memory and display them ? |
10/15/2018 6:34 PM | |
Joined: 10/7/2009 Last visit: 2/10/2025 Posts: 266 Rating:
|
Dear morylATCS, You don't need a special USB stick from SIEMSNS. Use a standard USB stick, just as Hati said:
The links for the manuals: |
Last edited by: Jen_Moderator at: 10/16/2018 7:46:51 AMOptimized links. |
|