Hi Hohetatran, Try to use: Press and Release options, and the Set function for press and the Reset function for Release. |
1/9/2019 9:01 PM | |
Joined: 1/11/2009 Last visit: 1/14/2025 Posts: 13 Rating:
|
It looks to me that you use a tag where HMI writes to as an IN/OUT variable of FB. You should not do that because HMI runs asynchronous from PLC in S7-1200/1500 (unlike in S7-300). Read also this FAQ and also link in its Further Information section. |