Hello everybody. I have a question regarding HMI Panel PC Ex : 6AV7200-1DA34-0AA0 as below and it is to be used in Explosive area called Fuel(Petrol/Diesel) filling Station, to be fixed on the door of AEx ib marked panel. - CanI use Normal 24VDC for this HMI panel PC ? - CanI use normalethernet cable for its communication with PLC? -Is this HMI Panel PC hasBarcode Reader Interface ? If yesthen, can you provide me the connection detail ? |
Last edited by: AutoGen_405949 at: 12/4/2014 9:13 PM |
|
12/4/2014 9:56 PM | |
Posts: 1058 Rating:
|
Hello AutoGen_405949, see here for information: SIMATIC HMI Panel PC Ex/Thin Client Ex, Zone 1 SIMATIC HMI Panel PC Ex/Thin Client Ex, Zone 2 see chapter 7 - power supply, chapter 10.1 Installation and operation According ethernet cable the manual says: "Which cable cross sections are chosen should be decided on the basis of relevant regulations, such as DIN VDE 0298. Factors that might require a larger cross section, such as current, increased temperatures, cable bundling, etc. must also be taken into account !" regards |
12/5/2014 6:52 PM | |
Joined: 1/30/2013 Last visit: 12/14/2023 Posts: 3 Rating:
|
From The manual Ch-7, "Copper wires with cross sections of betwee 0.2 mm² (AWG 24) and 1.5 mm² (AWG 14) may be connected to any of the terminals of the operator interfaces." Is that mean I can use normal 24VDC supply for the HMI Panel PC or Not? For the Ethernetconnection also same thing also applicable, is that means i can useCAT5 / CAT6 cable for that? Also provide me the Reader interface connection detail(Port X8) |
Last edited by: DD_2014 at: 12/9/2014 1:47 PMIs anybody there to help me on my queries regarding HMI Panel PC Ex - supply and communication ? |
|