3/19/2017 8:15 AM | |
Joined: 2/6/2015 Last visit: 9/16/2024 Posts: 61 Rating: (19) |
Dear Adham.nagy, The card will only be for PLC as the HMI KP300 supports neither MM(Multimedia) nor SD(Secure Digital) Card. Also, It does not have USB support so no possibility to send a backup file that could be restored. One option that I can suggest you is to create a "Pack & Go" which can be used to load project from PG/PC to HMI using ethernet without needing the TIA installed. However, you will need to install two microsoft components that too are available for free. Remote Access to SIMATIC HMI Control Panels Hope it helps... Best Regards |
Kaushal Kumar Joshi |
|
3/21/2017 9:49 AM | |
Joined: 1/30/2006 Last visit: 9/16/2024 Posts: 310 Rating: (58) |
Well, you can make a back up of the KP300 on the S7-1200 Memorycard as of V12 on the KP300. I have attached some images off the screens on the KP 300 BR.-Sven AttachmentKP300.pdf (212 Downloads) |
Last edited by: SMJE at: 3/21/2017 9:50:04 AMBR. Sven |
|