1/27/2014 3:54 PM | |
Posts: 767 Rating: (69) |
Hello, Does anybody know how you can connect an HMI touchpanel and a WinCC Runtime together on 1 PLC? On both screens i must be able to change values.
|
1/31/2014 1:55 PM | |
Posts: 1299 Rating: (136)
|
Hello, that's the correct way to build a pc application. did you change the computer name and theIP adress of IE general? K!ke |
1/31/2014 3:06 PM | |
Posts: 767 Rating: (69) |
The IP of the PC and the IEgeneral are the same. 192.168.0.5 it looks normal to me.
|
1/31/2014 3:27 PM | |
Posts: 1299 Rating: (136)
|
The ip has to be the one you use on the pc with runtime advanced. and it has to be in the same subnet as the plc and panel. K!ke |
Follow us on