Hello This could be a good tip because in newer FW Versions of the PLCs there is used a secure HMI Communication setting in the Security settings of the PLC. If its active there is used a custom certificate for communication and this has a validitiy date. So the Date/Time has to be set properly on PLC and HMI. -> Some words to the License. For Simulation you will not need a runtime license. It will work also if a License box comes up: https://support.industry.siemens.com/cs/ww/en/view/109810854 (only if you run a Advanced RT on a productive system and not in silulation you should use the proper RT Licenses) PGPC Interface setting could also be the problem as suggested. If you are not sure, then please send a Screenshot from PGPC Settings and the connection editor in your HMI Project where we can see the connection details like Access Point Bye Murof |