8/13/2013 10:05 AM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
Hi KOSTA EA, I do not think this panel has the MPI port, I think that most have an ethernet port, or RS 485. |
8/13/2013 9:13 PM | |
Joined: 9/27/2006 Last visit: 3/23/2025 Posts: 12344 Rating:
|
Hello all; From the Weinteck website, the datasheet of the MT6050i: http://www.weintek.com/Download/MT8000/eng/DataSheet/i_series/MT6050iV2WK_DataSheet_ENG_110512.pdf It is stated: Com1 RS485 supports MPI 187.5K So basically, the MT6050i can act as a MPI master, simply connect to the CPU's MPI port with a RS-485 cable (prefered, Profibus cable and connectors) and follow the instructions for tag inport and connections from this manual (page 838): http://www.weintek.com/Download/eMT3000/eng/UserManual/PLC_connection_guide.pdf |
Last edited by: dchartier at: 8/14/2013 6:04 PM |
|