Hello, Let me disagree with Tagolover. It is not possible to use hot swap with S7-300 CPUs and ET200M without profinet. As the in case of insert or remove any module OB83 is called. And this OB is not supported by S7-300 CPUs. But there is also a way, or let me call a trick as H-H mentioned once
Please have a look on thisthread Hope this helps.
|