1/29/2009 2:38 PM | |
Joined: 9/27/2006 Last visit: 6/29/2024 Posts: 12264 Rating:
|
Hello Iyyappan S; The value 27648 has simply been selected as the maximum normal range value of any analog signal transfered to the CPU by a Siemens analog module.This numerical value is independant of the resolution of the particular analog module used (this is a way to standardize all scaling of analog readingsin the processor) For unipolar data, this would mean 0 to 27648 represents full range; above 27648, overrange, below 0, underrange.See the attached illustration for the equivalent numeric values iof a 4-20 mA or 0-20 mA signal. The basic configuration of the analog modules is best explained in the S7-300 module Data manual: http://support.automation.siemens.com/WW/view/en/8859629 Look at the chapters on Principles of Analog value processing and Representation of the analog values of analog modules. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 1/29/2009 2:40 PMLast edited by: dchartier at: 1/29/2009 2:40 PMLast edited by: dchartier at: 1/29/2009 2:40 PM |
|
This contribution was helpful to
29 thankful Users |
1/29/2009 5:27 PM | |
Joined: 10/12/2006 Last visit: 5/7/2024 Posts: 206 Rating:
|
Hi, read this in technical forum ... Analog Value regards zenta |
2/4/2009 8:39 AM | |
Joined: 12/6/2006 Last visit: 6/12/2024 Posts: 92 Rating:
|
Dear Mr.Ayman Elotaify, Thanks Very Much Regards Iyyappan S |
2/4/2009 9:13 AM | |
Joined: 5/28/2008 Last visit: 6/29/2024 Posts: 4510 Rating:
|
Hello Iyyappan, You are welcome. Greatings. |
Ayman Elotaify |
|
This contribution was helpful to
2 thankful Users |
6/17/2009 11:29 AM | |
Joined: 4/19/2008 Last visit: 6/25/2024 Posts: 1525 Rating:
|
Hi, Please find the attachement in that you can find the answer for Analog Value. Ammy AttachmentAnalog Module.pdf (7957 Downloads) |
Ammy |
|
This contribution was helpful to
11 thankful Users |
5/30/2010 7:41 PM | |
Posts: 6 Rating:
|
thank you very much MR.Ayman |
Follow us on