2/22/2018 4:37 PM | |
Joined: 4/24/2006 Last visit: 2/7/2025 Posts: 8839 Rating:
|
Hello Amir HF, Do you have the original HMI project? What panel do you have? Best regards, Wizard |
2/22/2018 6:13 PM | |
Posts: 4 Rating:
|
Hello wizard I do not have original HMI program. i just have program in HMI. My HMI is Simatic panel TP177B PN/DP-6anks, Thanks |
2/22/2018 6:14 PM | |
Posts: 4 Rating:
|
Hello ChristophD, My HMI is Simatic panel TP177B PN/DP-6anks, Thanks |
2/23/2018 6:28 AM | |
Joined: 5/12/2006 Last visit: 2/6/2025 Posts: 22526 Rating:
|
Hello, the TP177B is in the list and support backtransfer if it was enbaled during commissioning. Install WinCC Flexible and try to backtransfer the data. https://support.industry.siemens.com/cs/ww/en/view/21907703 Regards Christoph |
This contribution was helpful to
1 thankful Users |