1/25/2010 1:05 PM | |
Joined: 5/28/2008 Last visit: 6/6/2024 Posts: 1343 Rating: (141)
|
A value in array is nothing more then a "normal" value. You can also connect a array-variable to a graphic in HMI. But this don't solve the problem with saving the value for a long peroid. Here is a FAQ, which is nearly to your problem. But I don't like this method: How can you back up parameters before loading a new control program? Another way could be, to connect your S7-1200 with a OPC-Server. As OPC Client you can take MS Excel, there you can save your value in a table. After turning on your S7-1200 again after 3 month, you can write the last values from Excel to PLC. Hope it helps a little bit more.. regards |
1/25/2010 1:22 PM | |
Posts: 65 Rating: (2) |
Thank you very much, Robster! I'll try it all. |
1/27/2010 4:00 PM | |
Joined: 9/23/2005 Last visit: 6/8/2024 Posts: 4343 Rating: (1430)
|
Hi, the TP277, MP277, MP377 and Runtime can work with Historical Data. If they are homologated for S7-1200, that is other history... The FAQ http://support.automation.siemens.com/BR/view/en/38111886shows how to configure a Runtime with S7-1200. The same principle shouldwork with others HMI. |
Denilson Pegaia |
|
12/4/2015 1:00 PM | |
Joined: 9/1/2005 Last visit: 5/14/2024 Posts: 4101 Rating: (194) |
New question published by Ted_ng is split to a separate thread with the subject read value from sensor - How to save value with is not depend on time?. Best regards |
My Forum is the place to personalize your profile, |
|