1/15/2017 12:21 PM | |
Posts: 23 Rating:
|
HOW CAN I USE MODBUS RTU WITH ASCII TO CONTROL VFD. BECAUSE SOME INVERTER USE RS 485 ASCII . |
1/15/2017 3:25 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
Hello, In other words, you do not use Modbus RTU to emulate Modbus ASCII. Pay attention: The link says that the ASCII Modbus Driver does not support the new CP's with order number: 6ES7341-1.H02-0AE0 Have also a look to the FAQ CP340/CP341 Multi-Station polling based on ASCII driver protocol |
Best regards |
|
1/16/2017 8:16 AM | |
Joined: 4/28/2015 Last visit: 3/26/2025 Posts: 10836 Rating:
|
HelloAutoGen_76109, pls be clear about that ASCII, you mean MB ASCII or implement user defined ASCII protocol frames to RTU? This is important. |
With best regards... |
|
1/17/2017 9:46 AM | |
Posts: 23 Rating:
|
modbus rtu |
1/17/2017 11:34 AM | |
Posts: 23 Rating:
|
sorry about that. My q? I have vfd micno and I want to communicated with vfd . modbus rtu rs 485 Attachmentmicno vfd.pdf (158 Downloads) |
1/17/2017 12:12 PM | |
Posts: 3093 Rating:
|
just use the sample Duris recommended |
1/17/2017 1:57 PM | |
Posts: 3093 Rating:
|
Did you check the online help / manual for MB_Master parameters? There you can find the description. |