11/29/2019 1:47 PM | |
Joined: 5/20/2019 Last visit: 6/5/2022 Posts: 3 Rating: (0) |
hello sir , I have two HART based Differential pressure Transmitter.Which signal modules support these modules? |
11/29/2019 4:37 PM | |
Joined: 9/27/2006 Last visit: 4/23/2024 Posts: 12257 Rating: (2665) |
Hello Sundar; Siemens offers HART modules (AI and AO, point-to-point HART modules) in the eT 200M and ET 200SP (HA) range: SIMATIC ET 200M distributed I/O device HART analog modules https://support.industry.siemens.com/cs/us/en/view/22063748 SM 331; AI 8 x 0/4...20mA HART : 6ES7331-7TF01-0AB0 SM 332; AO 8 x 0/4...20mA HART : 6ES7332-8TF01-0AB0 SIMATIC ET 200SP HA Distributed I/O system https://support.industry.siemens.com/cs/us/en/view/109747953 ET 200SP HA, AI 16xI 2-WIRE HART 6DL1134-6TH00-0PH1 ET 200SP HA, AI-DI16/DQ16x24VDC HART 6DL1133-6EW00-0PH1 The attachment below shows a sample configuration for the ET 200M HART modules, notice the S7-400 CPU, the IM 153-2 Profibus interface module for ET 200M configuration, the HART modules as part of the ET 200M station, and the suggestion of Simatic PDM as a field device configurator for HART sensors and actuators. Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |