1/8/2022 6:50 PM | |
Joined: 12/19/2021 Last visit: 1/9/2022 Posts: 19 Rating: (0) |
Hi, this is what I have done but it behaves strangely. AttachmentLOGO!Soft Comfort Demo version - 3-point_step_controller_0BA8.Standard_DT.pdf (436 Downloads) |
1/8/2022 6:54 PM | |
Joined: 12/18/2014 Last visit: 7/20/2024 Posts: 33380 Rating: (4143)
|
Please don't upload a PDF file. Upload your LSC program as a ZIP file. |
1/8/2022 7:08 PM | |
Joined: 12/19/2021 Last visit: 1/9/2022 Posts: 19 Rating: (0) |
Ok, here the ZipAttachment3-point_step_controller_0BA8.Standard_DT.zip (406 Downloads) |
1/9/2022 6:35 AM | |
Joined: 12/18/2014 Last visit: 7/20/2024 Posts: 33380 Rating: (4143)
|
Try this.
Attachment3-point_step_controller_0BA8.Standard_DT_V2.zip (443 Downloads) |
1/9/2022 9:28 AM | |
Joined: 12/19/2021 Last visit: 1/9/2022 Posts: 19 Rating: (0) |
I forget to mention that the Logo supply will be 24VDC |
1/9/2022 9:36 AM | |
Joined: 12/18/2014 Last visit: 7/20/2024 Posts: 33380 Rating: (4143)
|
LOGO! 24CE, order number 6ED1052-1CC08-0BA1. AttachmentLOGO! 8 manual 0BA8 2021_05 xxxx8-0BA1 pages 335+336.pdf (420 Downloads) |
1/9/2022 9:39 AM | |
Joined: 12/18/2014 Last visit: 7/20/2024 Posts: 33380 Rating: (4143)
|
For the temperature measurement: What hardware do you use? PT100/1000 with the AM2 RTD modul? |