12/14/2023 1:04 PM | |
Joined: 6/20/2017 Last visit: 5/20/2024 Posts: 331 Rating: (31) |
Basically, when the electric circuit feeding current to a coil is opened, the current cannot cancel or change in value in zero time; it can only quench and vary by discharging the energy stored by the coil. Consequently, the electrical potential of the coil will be forced to assume any useful value, (depending on the impedance over which the current will be able to flow). I foundthis paper, with particular reference to Figure 8. The blue line, current, as you see, when you open the circuit does not cancel and, therefore, the coil potential, red line, reacts to varies until somewhere it manages to discharge the current. Even at the cost of producing electric arcs. (But this is not our case, because as we said the recirculating diodes send the extra potential back to the DC bus, the capacitors on it then absorb some of the energy, etc., etc., etc. |
Last edited by: Gustavo Banchetti at: 12/14/2023 13:08:43Last edited by: The Helping Hand at: 12/14/2023 13:15:07Text formatting optimized Herr Gustavo Antonio Banchetti Brucatori. |
|
This contribution was helpful to1 thankful Users |