9/12/2010 3:03 PM | |
Joined: 7/28/2010 Last visit: 8/31/2024 Posts: 184 Rating: (11) |
Kasper, 1. You should use RTD-2L in Hardware Config for Measurement Type for the 5th AI channel. 2. Take a look at the attached file for Analog Value Representation and see if you get the right value. Regards, Behnam www.sigmaprocess.ca/blog AttachmentAnalog Value Representation.pdf (327 Downloads) |
9/12/2010 5:20 PM | |
Joined: 3/21/2006 Last visit: 9/10/2024 Posts: 10228 Rating: (1181) |
Hello, Perhaps this FAQ is helpful - How can you increase the resolution of temperature measurements using PT100 via the integrated analog input of the CPU 31x C? Best regards, Hristo Mihalev |
This contribution was helpful to1 thankful Users |
9/23/2010 1:29 PM | |
Joined: 7/28/2010 Last visit: 8/31/2024 Posts: 184 Rating: (11) |
Kasper, Results sound good. (0 C) = 0x0 = Decimal 0 (25,7 C = 0xF0 = Decimal 240 = 24.0 C (51,6 C) = 0x1F0 = Decimal 496 = 49.6 C (77,7 C) = 0x2F0 = Decimal 752 = 75.2 C (130,4 C) = 0x4F0= Decimal 1264 = 126.4 C (322 C) = 0xC80= Decimal 3200 = 320.0 C Regards, Behnam www.sigmaprocess.ca |
9/23/2010 2:19 PM | |
Posts: 39 Rating: (1) |
Hello Thank you for your answer, but I hoped for at more accurately result - something like 0,1 degree celcius. Is it possible to change the resolution? Kasper |
9/23/2010 6:29 PM | |
Joined: 7/28/2010 Last visit: 8/31/2024 Posts: 184 Rating: (11) |
Kasper, Based on the Standard, the sensitivity is 0.385 ohm/°C. You are off on all values and it is kind of consistent except the last one which is way off. If theoffset is going to be consistent in the range you need, you can addor deduct the offset and get your result. There are couple of sources for error too. Check out the article in Wikipedia for RTD. http://en.wikipedia.org/wiki/Resistance_thermometer Regards, Behnam www.sigmaprocess.ca |