Hi, How do you configure alarms in s7-1200 and ktp400? I got used to s7-300 way: In step7 basic i have bool tags in DB alarm ex. db1.dbx0.0 alarm 1 ..... In ktp400 i cant declare db1.dbw0 as alarm word. in step 7 basic also a i can't move db1.dbw0 to db1.dbw2 AlarmWord Why step7 basic doesn't allow me to access to non symbolic tags? (access symbolic access is off for DB1) For now i maybe use the ex. program to move bools to tags. But its strange way a think best regards Splitted from Is it possible to change DB's 'symbolic access only' to tags after it was created?. |
Last edited by: O_Moderator at: 9/14/2010 11:22 AMnew subject after splitting |
|
9/14/2010 2:57 PM | |
Joined: 6/29/2010 Last visit: 10/27/2022 Posts: 112 Rating: (63) |
Hi, You can select a variable of type word at DB and specify the trigger bit of the word. Take a look atthe pictures attached. Good luck. AttachmentS7 Basic Alarms.zip (3085 Downloads) |
10/1/2010 5:37 PM | |
Joined: 6/29/2010 Last visit: 10/27/2022 Posts: 112 Rating: (63) |
Hi fbelic, |
10/1/2010 6:01 PM | |
Posts: 327 Rating: (28) |
Thanks, this is a good idea! Best regards
|
10/4/2010 4:08 PM | |
Joined: 10/22/2008 Last visit: 9/22/2024 Posts: 369 Rating: (5) |
Thats the olny way i know for now too. Convert all bits to word with this FC. |
10/23/2020 3:58 PM | |
Joined: 8/11/2015 Last visit: 5/24/2024 Posts: 13 Rating: (4) |
My solution for alarm:-) Watch video |