3/28/2014 8:49 AM | |
Posts: 2 Rating:
|
I need to upload the data from the DB from S7 300 (CPU 314C-2DP) into DB S7 400 via Profibus. Please tell me how to do this? Are there any examples? |
3/28/2014 10:07 AM | |
Posts: 1368 Rating:
|
Hello, the solution are the PUT/GET blocks. Look here at this overview http://support.automation.siemens.com/WW/view/de/78028908 Examples are here: http://support.automation.siemens.com/WW/view/de/1020634 http://support.automation.siemens.com/WW/view/de/1819293 http://support.automation.siemens.com/WW/view/de/22867279 ... Have fun! Edit: Additional Options are here described http://support.automation.siemens.com/WW/view/en/25534113 |
Last edited by: Pittiplatsch at: 3/28/2014 1:40 PM |
|
This contribution was helpful to
1 thankful Users |