i am working with a logo 230 RCL, how is the conection for the inputs, are they P or N? Splitted from NPN inputs. |
Last edited by: O_Moderator at: 9/30/2010 10:40 AMnew subject after splitting |
|
10/3/2010 11:53 PM | |
Joined: 7/28/2010 Last visit: 8/31/2024 Posts: 184 Rating:
|
Solorzano, It is AC input. There is no such a thing as PNP or NPN. Hook up one side to N, pass the other side through your switch to the input. Regards, Behnam www.sigmaprocess.ca |