1/11/2017 10:30 AM | |
Posts: 4 Rating:
|
Hello all, Following your discussion, I would like to ask how many connections with S7-1200 can handle a S7-1500¿? How many connection resources are needed to stablish a link between them¿? I working on a project in which a single S7-1500 PLC must control at least 30 S7-1200 remote units. Best Regards ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 1/11/2017 1:37:49 PMNew subject after splitting |
|
1/11/2017 2:01 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
|
hi AGEnes, when you do it with I-Device-solution, you don´t need connection resources. The S7-1200 would be a device of the S7-1500 over Profinet. And a S7-1500 can handle up to 256 Profinet-devices over the internal interface. Have a look: Configuration and application of PROFINET I-Device function hope this helps, regards |
FCK WAR! |
|
2/16/2017 2:31 PM | |
Posts: 4 Rating:
|
Hi, 1511 and 1513 - up to 128 connections 1515 ... - up to 256 connections. Good to know when using for example distributed IOs over profinet :) |