Dear All, Please i want to know how many KTP 700 Basic HMI I can connect to S7 1200 PLC (CPU 1214 AC/DC/RLY) Thank you |
11/23/2018 12:08 PM | |
Joined: 12/13/2011 Last visit: 10/1/2024 Posts: 146 Rating: (6) |
hello I'm not sure, but I think it will work to the maximum of the screen variables ktp700 will be about 800 |
11/23/2018 12:45 PM | |
Posts: 27 Rating: (0) |
Thank You javiermorales I have connected 6 HMI's (KTP 700 Basic), HMI - PLC response is slow. But when I connect 4 HMI, it is normal. As per Siemens Blog, the response will be normal for 4 HMI. Pfb link https://support.industry.siemens.com/cs/br/en/view/38051505 Can you please tell me about this? Also what is connection resource? Is it "1 HMI = 1 connection resource" ? |
Last edited by: Jen_Moderator at: 11/26/2018 8:46:41 AMOptimized link. |
|
11/23/2018 7:57 PM | |
Posts: 2826 Rating: (688) |
Hello.
The FAQ (ID 38051505) states that there are 3 classes of HMI: The FAQ states further that Siemens guarantee at the very least 4 HMI connections irrespective of which HMI combination you use. The capacity of the PLC is 12. The theory is you can use 12 basic HMIs. There is no mention to what is practical. I will not be able to tell you this. Factors that will influence the effectiveness of communications:
BR |