The CPU that I'll use is the 6ES7511-1AL03-0AB0 SIMATIC S7-1500, CPU 1511-1 PN. |
5/24/2023 4:56 AM | ||||||||||
Joined: 3/11/2019 Last visit: 9/27/2023 Posts: 1004 Rating:
|
Hi, as mentioned. Technical data. 6ES7511-1AL03-0AB0CPU 1511-1PN, 300KB Prog., 1,5MB Data
Max possible connections via integrated interfaces (without CM/CP) = 88 -> 78 connections can be used dynamically These are shared ressources, it doesn't matter if Modbus/EthernetIP (all based on OUC) or S7-communication. regards sancruz |
|||||||||
Last edited by: sancruz at: 05/24/2023 04:58:02Feedback appreciated, please rate |
||||||||||
This contribution was helpful to
1 thankful Users |
5/25/2023 3:28 PM | |
Joined: 5/6/2018 Last visit: 9/27/2023 Posts: 13 Rating:
|
Thanks for clearing it out |