Hello A9K as TEBANCHquite rightly said, we would need more detail about your system to give you the correct advise. Nonetheless, you say that you five 100U's all networked together. The only way this could be done would be via SINEC L1. What seems missing though is a SINEC L1 Master (a 100U can only be a SINEC L1 Slave). Can you please clarify what type of system architecure and network Topolgy you exactly have (draw a little sketch that shows the type/aprt numberof CPU',CP's, netwrok componentsetc.). In case it is a SINEC L1 Network, I suggest youalready start studying the two manuals below which contain all the info on how to set it up and what to look for in the program. This will then help you determine if you perhaps already have a free/spare Datword in the exisitng communication that you could then simply use to put your Furnace tilting angle in. Local Area Network SINEC L1 manual S5-100U Programmable Controller manual I hope this helps |