4/10/2024 5:55 AM | |
Posts: 1 Rating:
|
Hello, In Wincc Unified parameter there was a edit tag, how should I use that any idea about that, siemens provide an document they mention sessional local tag is used for Edit Tag, I was create Internal tag but it wont be support ------------------------------------------------------------------------------------------ |
Last edited by: jeyasingh_b1330 at: 04/10/2024 05:59:04Last edited by: Jen_Moderator at: 04/10/2024 09:23:11New subject after splitting |
|
4/11/2024 5:53 AM | |
Joined: 1/21/2013 Last visit: 4/17/2025 Posts: 3761 Rating:
|
Hi jeyasingh_b1330, The edit tag for a parameter set must be a local session HMI tag with the same number of elements and data type as the tag used for the parameter set. It is used to create a custom solution in place of the default parameter set control. The edit tag allows a parameter set to be modified without changing the values inside the PLC. However, you must use scripting to transfer data from the edit tag to the parameter set. See section 4.17.4.2 of the "Guide for switching from Comfort Panels to Unified Comfort Panels". Kind regards |
This contribution was helpful to
1 thankful Users |
4/12/2024 7:40 AM | |
Joined: 8/3/2009 Last visit: 4/17/2025 Posts: 15311 Rating:
|
Hello jeyasingh_b1330 There should also be an example in the V18 Demo Project: https://support.industry.siemens.com/cs/de/en/view/109822799 Bye Murof |