12/18/2020 12:16 PM | |
Joined: 9/27/2006 Last visit: 4/27/2024 Posts: 12257 Rating: (2665)
|
Hello Saeed; You have 2 questions here: - why 16#8000 from your sensor reading? An overflow reading probably comes back to sensor connection on the Analog Input card, or a wrong configuration of the sensor. Do you know what the sensor is (make and model) and how it is configured in Step 7 HWConfig? - why is your HMI showing ##### instead of a scaled value for your PIW5xx sensors (your OUT3)? A Siemens HMI uses tags to connect to the PLC over a selected communication channel. You place an input IO Field in your screens to display these tag values (coming from the PLC). If the tag is not connected to the CPU (your comm channel is down) all IO Fields will display #####. If the value to display is larger than the size of the IO Field (too many digits to display) then this particular IO Field shows #####. Try enlarging the IO Field in your screen by dragging it bigger. There are many discussion here on the subject, here is one; https://support.industry.siemens.com/tf//ae/en/posts/hmi-values-shows/244068/?page=0&pageSize=10 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 12/18/2020 12:22:16 |
|
This contribution was helpful to1 thankful Users |
12/20/2020 1:56 PM | |
Posts: 39 Rating: (0) |
Hello Daniel Thank you so very much for your reply and concern. I highly appreciate your response I am attaching herewith this post the original FC6 content ( printed, please see the pdf). I have marked the changes I made in a blue pen Also, I have split the networks i.e each FC6 in now in a standalone network NW27,28, and 29 because I can not see the point of making them in one network so if one fails the other two one follow suits I am forward to hearing your comments on changes I made plus how to get the ENO of the left FC6 activated so to enable the second and the third ( in case I left them all in one NW) Regards AttachmentFC6 content 1.pdf (147 Downloads) |