Hi. Terminal 112 can only be used for SIMODRIVE 611 analog and |
9/29/2008 9:33 AM | |
Joined: 9/18/2006 Last visit: 3/19/2023 Posts: 583 Rating:
|
Hi. I have found something in the old documentation. When changing–over from normal operation, terminal 112 energized, into setting–up operation, terminal 112 de–energized, terminal 48 must also be de–energized, either earlier or at the same time. After the internal line contactor has dropped–out, the setting–up voltage can be connected to the power circuit terminals. Setting–up voltage 34 V...600 V DC or 3–ph. 24 V...3–ph. 420 V AC (refer to Section 9.5). For setting–up operation, the DC link control in the I/R module is inhibited. The DC link voltage obtained, is the rectified line input voltage; regenerative feedback is not possible (VDC link can exceed to over 600 V when braking!). It can to you will help. Successes. AttachmentTerminal 112, version 2.pdf (104 Downloads) |
9/29/2008 9:40 AM | |
Posts: 672 Rating:
|
Hi, Thanks again but terminal 48 was de-energised. I pulled out the connector to put the link in |