2/26/2021 9:26 AM | |
Joined: 4/28/2015 Last visit: 9/20/2022 Posts: 1278 Rating: (295) |
Hi, ok I see the load cell is moved by 2 axes in synchronous operation and you want to put pressure on the fabric. Please see chapter 3.10.4 in this manual: https://support.industry.siemens.com/cs/de/en/view/109766462 For positioning and Synchronous axes you can use the TorqueLimiting function. This automatically disables the following error detection and makes it possible to move against a mechanical fixed stop with a defined torque (limit). So as described above you have your TO PosAxis (Master) and the TO SyncAxis (Slave). With the GearIn command you can synchronize the slave to the master. Then you give a position setpoint to the master which is beyond the mechanical stop (so it tries to go further but cannot reach the target). Doing that movement you also activate the MC_TorqueLimiting function on both axes and give your required torque limit as a parameter. So the load cell will push against the fabric with a defined torque/force. |
Best regards, |
|