9/15/2016 12:05 PM | |
Joined: 10/11/2006 Last visit: 1/22/2025 Posts: 5985 Rating:
|
Hello, the stop cams are activated via POS_STW2 bit 15 of telegram 111. Because of this selection the parameter p2568 is already connected with r2092.15. To activate the stop cam you have to send a true signal on POS_STW2 bit 15. If you want to send the stop cam signals from your PLC with PZD 12 (user) you have to connect r2050[11] to r2099[x]. After this you can connect the parameters p2569 and p2570 to the corresponding parameter r2094.xx or r2095.xx to receive the single bit from the PLC, the stop cam function is activated with a low signal on p2569/p2570. Additional information could be found in the function manual basic positioner. AttachmentList Manual G120 CU250S-2.pdf (389 Downloads) |