1/17/2016 6:49 PM | |
Posts: 1 Rating:
|
Hi everybody, I need to provide a cabinet with an ET200S system. However I am an electrician technician, not an automation one, and I have some difficulties to understand how to wire analog signals. I have a "AI 8xI 2-/4-wire BA" card (6ES7134-6GF00-0AA1) with a A0 type base unit. My 4-20mA signals is coming from an active sensor (in fact from the output of the enclosed material). From what I understand, the "AI 8xI 2-/4-wire BA" is an active input and it should not be possible to connect active sensor to active PLC input... May you please help me to understand how should I wire the input signal to the AI module? Thanks in advance PS: sorry for my english, I am French... AttachmentPR 3109.pdf (309 Downloads) |
1/19/2016 12:38 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
|
hi lyuum, in following Link you find a download of ET200SP manual collection.(also available in french ;) ) SIMATIC ET 200SP Manual CollectionIn the second part of the manual collection you will find the specific manual of the AI8xI 2-/4-wire module. In chapter 3 you find the wiring and block diagram. Your mesurement should be a 4-wire connection. hope this helps, regards, |
FCK WAR! |
|