7/24/2019 9:20 PM | |
Joined: 9/27/2006 Last visit: 3/17/2025 Posts: 12344 Rating:
|
Hello nourish; You will need a 20-COMM-P Profibus interface adapter installed on your Powerflex 700 to make it a Profibus-DP slave node that the S7 CPU can control. Here is the link to the 20-COMMP manual: https://literature.rockwellautomation.com/idc/groups/literature/documents/um/20comm-um006_-en-p.pdf And here is an application note showing how to configure and program a CPU 315-2DP as a Profibus master to a Powerflex 700: You might have some difficulty in locating the 20-COMM-P gsd file (needed to insert a 20-COMM-P as a Profibus slave in a master's configuration). All the links I have now lead to a Sign-In page for Rockwell's Automation Account site. I do not have this access to request the gsd file. Do you? Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 07/24/2019 21:22:42 |
|
7/24/2019 9:45 PM | |
Posts: 111 Rating:
|
To follow-up the detective work - search fo "20-comm-p" on the RA site |