Hi, unless the NJ or OMRON blocks the PING requests, it seems that the NJ doen't pass TCP telegrams. So it will not be possible to reach the OMRON. One solutin would be to rewire the network, that you have a direct line to the OMRON PLC and not just "through" the NJ. |
iba AG - Data Acquisition and Analysis the way it should be |
|
This contribution was helpful to
1 thankful Users |
7/26/2019 2:11 PM | |
Posts: 15 Rating:
|
Yes, thanks for your reply, we are considering using a spare NIC adapter in the server to directly connect to the PLC side. We'll see...:) Thanks |