12/11/2019 1:59 PM | |
Joined: 9/27/2006 Last visit: 5/11/2024 Posts: 12257 Rating: (2666) |
Hello Boris; You have 3 nodes in your network, 2 end-nodes (one at each end of the network) and one middle-node. It does not matter where you have the PLC in this situation, it can be an end-node or a middle-nide. Profibus-DP uses a daisy-chain (line connection) as shown in the attachment below. Start with your connector (with one cable only) , run the cable to your middle-node with 2 cables(one entering, one leaving the connector) and finish on the other end-nide. Termination resistors should be ON for each end-node, and OFF for the middle node. The screenshot was taken from the Profibus design manual, from profibus.com, as part of the Profibus installation guidelines collection: https://www.profibus.com/download/profibus-installation-guidelines/ Hope this helps, |
12/11/2019 3:51 PM | |
Joined: 12/14/2018 Last visit: 5/2/2023 Posts: 41 Rating: (3) |
Thank you Daniel for answer. I have only 3 nodes and 3 cables from it. I cannot change connection inside node. In this situation - what can i do? Maybe this scheme will work? |
Last edited by: Boris M at: 12/11/2019 15:59:47Last edited by: Boris M at: 12/11/2019 16:09:40 |
|
12/11/2019 5:22 PM | |
Joined: 12/14/2018 Last visit: 5/2/2023 Posts: 41 Rating: (3) |
Thank you Daniel for T-Junction! |