12/19/2019 7:16 PM | |
Posts: 17 Rating: (0) |
No answer my friend? Also I need to know how to connect PT100 in module AM2 RTD and also if you use AI as "in" for PT100. Do you solve this information? Thanks for support ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 12/20/2019 08:27:59New subject after splitting |
|
12/19/2019 7:33 PM | |
Joined: 12/18/2014 Last visit: 9/25/2024 Posts: 33835 Rating: (4205)
|
For wiring see the attached PDF. For addressing: Normally in the LOGO! base modul are the adressess AI1 and AI2 reserved for the base modul. If you don't need AI's on the base module or the base module has no AI's then you can select the default setting to no AI's on the base module. File > Properties > Offline Settings > I/0 Settings. Or over the menu of the LOGO! directly. If no AI's reserved for base modul and the AM2 RTD is the first analog extended modul, then the addresses AI1 and AI2. If 2 AI's reserved for base modul and the AM2 RTD is the first analog extended modul, then the addresses AI3 and AI4. If 4 AI's reserved for base modul and the AM2 RTD is the first analog extended modul, then the addresses AI5 and AI6. AttachmentLOGO! 8 manual 0BA8 2017_11 xxxx8-0BA0 pages 49+50.pdf (570 Downloads) |
This contribution was helpful to1 thankful Users |
12/20/2019 1:44 PM | |
Posts: 17 Rating: (0) |
I have use PT100 with 2 wires BL and RD, so should I connect in U+ and U- ? And also I set AI1 to AI5 and nothing work. Can you give me more support? Thnks |
12/20/2019 1:57 PM | |
Joined: 12/18/2014 Last visit: 9/25/2024 Posts: 33835 Rating: (4205)
|
Have you make a bridge zwischen U1- und IC1? This is needed by 2wire PT's. |
12/20/2019 2:04 PM | |
Joined: 12/18/2014 Last visit: 9/25/2024 Posts: 33835 Rating: (4205)
|
Is the AM2 RTD the only analog expansion modul? What color is the RUN/STOP LED on the AM2 RTD? Red or green? |
12/20/2019 3:25 PM | |
Posts: 17 Rating: (0) |
Please check screen |
1/8/2020 5:49 PM | |
Posts: 17 Rating: (0) |
Hi my friend, can you recommend any brand for PT100 that I can find and use in my project? Of course I am looking a solution that give max of precision. |
1/8/2020 6:22 PM | |
Joined: 12/18/2014 Last visit: 9/25/2024 Posts: 33835 Rating: (4205)
|
I would suggest a 3 wire PT. Take a look perhaps by Amazon? |
1/8/2020 6:36 PM | |
Posts: 17 Rating: (0) |
Check if possible the attachment file. This brand is 3 wire WJE PT100 06x50mm 2meters |
1/8/2020 6:37 PM | |
Posts: 17 Rating: (0) |
Attached file PT100 we think to buy |
Follow us on