Hello Youmbah To Connect a S71200 it´s no Problem with V7.3 : https://support.industry.siemens.com/cs/ww/en/view/101908495 Also you can create 3 connections, but the main thing is you wrote you want to write "at the same time". This is not possible. The HMI communication is not proceeded in the normal S7 cycle. It works parallel to the S7 PLC cycle. So you cannot be sure that a Tag is written simultaniously to all three PLC Connections. But it you only want to write to all three this is no Problem. Bye Murof |
If this Information really helps, you could use the Rate function |
|
This contribution was helpful to
1 thankful Users |
10/25/2018 2:13 PM | |
Joined: 11/20/2015 Last visit: 10/4/2024 Posts: 25 Rating:
|
Thanks murof for your link, it was helpful too, I am able now to read tags and control the system
|