Industry Online Support
Technical Forum
6/17/2009 2:13 PM | |
Posts: 88 Rating: (0) |
Hi Everyone I have Step7 V5.4 SP4 and WinCC V7.0 SP1 which are installed on a PC. I have created a multi project like in PCS7 and it contains PLC project and OS project. (While installing wincc, I have also installed AS-OS engineering) I created a FB it contains ALARM_8P and I used it in the OB1. When I compile the OS project, the tags that relates created FB, are created automaticly. But I could not create messages automaticly. I have read the document that is attached by me and I have done needed arrengement but could not create messages automaticly in the alarm logging. Attachmentsfb35 alarm logging.pdf (543 Downloads) |
6/17/2009 2:49 PM | |
Posts: 35 Rating: (0) |
Did you download the S7 program into the PLC? |
6/17/2009 2:52 PM | |
Posts: 88 Rating: (0) |
yes. I am using PLC sim and s7 program is online now |
6/17/2009 3:41 PM | |
Posts: 88 Rating: (0) |
CPU type is 314C 2DP. OS and PLC comm is ok. |
6/17/2009 3:55 PM | |
Posts: 261 Rating: (42) |
Hi cosmetric, You can go through with this document. SFB 35 is for 400 CPU regards ddg Attachmentalarm.pdf (530 Downloads) |
Last edited by: ddg at: 6/17/2009 4:01 PM |
|
6/17/2009 5:08 PM | |
Joined: 3/18/2009 Last visit: 2/8/2022 Posts: 306 Rating: (94) |
For S7 300 CPUs you have to use SFC17, SFC18, SFC107 or SFC108. ThisFAQgives you detailed procedure
|