Hello TEBANCH, as far as I remember FB125 dosn't work with a CP 342-5. You have to use the FC DP_Diag. It is part of the libary for this CP. Within the DPSTATUS of the DP_RECV you will get the information, that new diagnostic data exist. Details could be read with the other FC. Here you should found detailed information:
Good luck Sabine |