2/16/2017 11:29 AM | |
Joined: 7/15/2011 Last visit: 8/8/2024 Posts: 48 Rating:
|
HI, Right now I am using Op177B 6" Colour PN DP panel, I am facing an error called the device is not having enough memory, this message comes just after I download is complete. I am sure the memory consumption is not much, as the same software is working in other panels. I tried reset to factory after going through some of the forum, but I couldnt find the reset to factory setting check box in my pc, in prosave and also in Wincc. I tried with MPI cable and also ethernet cable, with MPI cable the transfer starts for update but in a sec it stops saying connection lost, with ethernet is says no enough memory. Can some tell me how to do reset to factory setting for above mentioned panel, check box is not found in my case. ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 2/16/2017 5:16:49 PMNew subject after splitting |
|
2/20/2017 10:27 AM | |
Joined: 5/28/2008 Last visit: 2/12/2025 Posts: 4518 Rating:
|
Hello, You can't use MPI and Ethernet cables to update OS for OP177B color PN/DP. Please use PPI cable (serial or USB type). Part numbers are as follows:
|
Ayman Elotaify |
|