11/6/2010 7:36 PM | |
Joined: 1/28/2009 Last visit: 5/2/2024 Posts: 6838 Rating: (1359) |
Check the attachment, I think this suffices you need to do your job. Refer To this manual for more detail. (Section 12-3) This is matter of preference, I always download program in master , read the Reasons in attachment. Best regards AttachmentPG.zip (813 Downloads) |
Last edited by: hdhosseini at: 11/6/2010 7:53 PM |
|
11/6/2010 9:14 PM | |
Joined: 7/2/2008 Last visit: 4/5/2024 Posts: 928 Rating: (305)
|
Hello umair, The answer depends on whether you have RAM orFLASH memory card. You can understand the difference by reading page 55 in the above linked manual by hdhosseini. I also recommend to read chapters 14.5 and 14.6. Briefly, if you have RAM cards then you can download to the master CPU and the standby one will beautomatically updated. This is not the case if you have FLASH memory cards. 1st you have to download when CPU is in STOP. 2nd you have to download to both CPUs (Automatic program update is not possible). You can download to CPUs with FLASH while they are running but the download will be targeting the work memory not the load memory. Once you restart the CPU, the unchanged program will be taken from load memory (FLASH) to the work memory and all changes will be gone. Best regards. H-H |
This contribution was helpful to1 thankful Users |
2/20/2011 6:12 AM | |
Posts: 1 Rating: (0) |
hello, i cant download the manual and zip file if its possible send me these files. thankyou. |