6/21/2010 11:05 AM | |
Joined: 9/18/2006 Last visit: 5/3/2024 Posts: 589 Rating: (64) |
Hi. I hope, that this chapter from the "Function Manual" will help you. Best regards AttachmentParameterizing using the BOP20.pdf (338 Downloads) |
This contribution was helpful to1 thankful Users |
6/21/2010 11:27 AM | |
Posts: 101 Rating: (8) |
Good luck!! You will need lots of it! I strongly recomend you do not bother and use the free starter software. |
6/21/2010 12:14 PM | |
Joined: 9/18/2006 Last visit: 5/3/2024 Posts: 589 Rating: (64) |
Hi. I agree. It will be more reliable to you to work with Starter or Scout. I hope the resulted document to you will help. You pay attention that motor witch DRIVE-CLiQ the interface. Best regards. AttachmentQuick commissioning using the BOP (example).pdf (230 Downloads) |
6/21/2010 12:51 PM | |
Joined: 9/18/2006 Last visit: 5/3/2024 Posts: 589 Rating: (64) |
Hi. I probably have hastened. This small addition. You pay attention on Commissioning requirement. I have not found Table 1-1 or table 1-2 from Section1.1. This documentation has order-number 6SL3097-4AB10-0BP1. Best regards. AttachmentInitial commissioning using servo AC DRIVE with BOP20 as an.pdf (189 Downloads) |
9/6/2012 8:57 PM | |
Posts: 2 Rating: (0) |
Could you tell me how to activate externel (may be extended)setpoint channel? Best regards, fitter |
9/7/2012 3:11 AM | |
Joined: 2/1/2010 Last visit: 11/22/2023 Posts: 25 Rating: (0) |
You can set the p0108[1].8 to 1 on DO1 Best Regards lin |
11/14/2016 11:37 AM | |
Posts: 21 Rating: (0) |
|