10/27/2011 4:31 PM | |
Posts: 5822 Rating:
|
Hello, well, I admit I am quit in this issue right now. With the MD 720-3 you will need to use a PC Station with a fixed IP or an DYN-DNS Address online at the Internet. This PC Station will then forward your data from PLC to PLC. On this PC you need either the - Micro SC Server, or - Telecontrol Server Basic. (check this for further information's http://support.automation.siemens.com/WW/view/en/16626992/133200) Best regards J_Bell |
This contribution was helpful to
1 thankful Users |
11/18/2011 8:02 AM | |
Posts: 21 Rating:
|
Hi, Can any one tell me or give me an example how to write protocol for communication between s7-1200 with cm1241 (RS232) and SINAUT MD720-3? |
12/14/2011 4:43 PM | |
Posts: 5822 Rating:
|
Hello, you are right, it will not work with the serial interface and the MD 720-3. Have you ever spend a thought on a CP 1242-7? These module may provide you a feature, but under special circumstances, look for GPRS direkt for more to know. Best regards J_Bell |
Last edited by: J_Bell at: 12/14/2011 4:49 PM |
|