Hello Darlam I'm afraid the HWconfig won't be able to tell you which PA device is connected to each of the 5 PA couplers. Reason being is that all of your5 PA couplers arebehinda singleDP/PA link and as such (and also as far as the PLC is concerned) there is only one PA Master system behind theDP/PA link. The advantage of being able to have up to 5 PA couplers behind a DP/PA link is simply to be able to have more than one physical PA segmentbehind the DP/PA link (which can be benificalfor reasons such ascurrent consumption segregation, spurline lenghts, number of PA devices per Segment etc.). I trust this helps in sheding some light on it,more useful info is contained in the DP/PA coupler/link operating instructions(I would haveattched the download link here but there is something wrong with the Siemens service & support web at the moment). Cheers Fritz |
Cheers |
|
3/4/2009 5:59 PM | |
Posts: 4 Rating: (0) |
Hi Daniel, Thanks for the suggestion, it will be helpful if I had something like that. For the moment I am still looking for my transmitter. Regards |