2/19/2012 9:48 PM | |
Joined: 10/7/2005 Last visit: 4/26/2024 Posts: 3004 Rating: (1046)
|
Hello YurArm while you can create an I-Slaves GSD file for Profinet I-SLaves, you unfortunately not do the same for a Profibus I-Slave. What you can do though is: 1.) Give the other company the general GSD file for your CPU (see HERE) 2.) They'll us this and then manually create the I/O config that needs to match yours (Note: You Inputs are their Outputs and vice versa) As you don't want to give them your program, I presume the your S7-300 and their S7 will NOT be integrated into one project, so the closest matching example is in the link below: How do you operate an S7-300/400 as a DP slave on the PROFIBUS DP when the DP master is an S5 (with IM 308-C)? In case you do decide to integrate the two projects into one, the alternative (and less error prone configuration) is described in the link below: DP link between CPU 315-2DP (slave) and S7-400 (master) with STEP 7 V5.3 I hope this helps |
Cheers |
|
This contribution was helpful to3 thankful Users |