3/29/2012 4:26 PM | |
Posts: 83 Rating: (1) |
yes the situation is like you described. |
3/29/2012 5:02 PM | |
Joined: 9/27/2006 Last visit: 9/16/2024 Posts: 12282 Rating: (2684)
|
Hello avafab; You could remove ("disable", "deactivate") the slave temporarily from the DP-master's call list by using SFC12. This would block communications with the slave until you reactivate it, so you coukl not use it on the network until reactivation. Couls you live with that option? What should you pay attention to when operating a DP slave temporarily on a PROFIBUS DP network? Notes for the use of the system function SFC12 "D_ACT_DP" Enabling a disabled DP slave with SFC 12 "D_ACT_DP" Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
3/29/2012 5:31 PM | |
Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328)
|
If the removed parts are in ET200 Stations you should have a look at this: http://support.automation.siemens.com/WW/view/de/29430270 |
|
|
This contribution was helpful to2 thankful Users |
5/4/2012 9:41 AM | |
Posts: 83 Rating: (1) |
Yes ET200s I followed the link and the problem is solved, I deactivated only those ET200s that are physically not connected. Thank you
|