Hello, You can do it very easily from starter or BOP. You just have to set parameter 50051 as required according to optimization type. Please refer section 8.7 of the manual. Just remember some points: - follow the sequence of optimization runs in order shown in manual. for ex. field optimization has to be followed by armature and then speed optimization. - after setting parameter p50051 give start command within 30 sec, remember motor will run for short time with jerk so load must be disconnected. - after successful optimization p50051 will automatically set to 0. Hope this helps. |