4/22/2021 11:44 PM | |
Joined: 7/7/2010 Last visit: 4/25/2025 Posts: 15822 Rating:
|
Read p2111 to get the number of faults that have not been acknowledged (reset). Use that # to index through the fault tables to get codes. Refer to List Manual, found here: List Manual S120/S150 (siemens.com) Go to page 2161. Refer to the function diagram on how to read out the faults. To me it looks like you use the count so you know how far to read into the fault buffers for "unack" faults, and the remainder of the fault tables are for ack alarms (old).
|
Last edited by: Jen_Moderator at: 04/23/2021 08:48:56Optimized link. science guy |
|