Hello pankaj_054, You can set 2 CDS & DDS i.e. command data set & drive data set independently. So 1 CDS with 1 DDS you can run DCM with electrical grid power supply & 2 CDS & DDS DCM can be run on diesel generator set. But please not, on diesel geneset, if input power supply is not within tolerances, drips will trip. |
This contribution was helpful to1 thankful Users |
12/25/2021 7:13 AM | |
Joined: 3/13/2019 Last visit: 11/6/2024 Posts: 174 Rating: (2) |
Thankx for replay......will u pls explain me in detail how can i set 2nd CDS or DDS in DCM set by step ????? |
12/30/2021 5:52 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating: (878) |
Hello, Regret for delay in reply since I was out of station. You can set CDS i.e. command data set as - CDS 1 data for electricity grid & CDS 2 for DG set. 4CDS available (p0810) Bit 0 = 0 & Bit 1 = 0 CDS0 Bit 0 = 1 & Bit 1 = 0 CDS1 Bit 0 = 0 & Bit 1 = 0 CDS2 Likewise set DDS p0821 for two different data set wherein you can set motor related data set. Please refer SINAMICS DCM, List Manual, Firmware version 1.5 (based on 5.1 SP1) manual chapter 3.18 Data sets. Hope this helps. |