10/25/2015 11:09 AM | |
Posts: 95 Rating: (0) |
hello how can I set the correct time , to sinamics so I can see the correct time in the alarm history ? thanks |
10/25/2015 12:09 PM | |
Joined: 5/12/2006 Last visit: 12/4/2024 Posts: 22472 Rating: (3035)
|
Hello, the Sinamics have no RTC so you must syncronize the Time with the PLC. How to do: https://support.industry.siemens.com/cs/ww/en/view/88231134 https://support.industry.siemens.com/cs/ww/en/view/60266999 Regards |
10/25/2015 2:48 PM | |
Posts: 95 Rating: (0) |
thanks Christoph suppose I am using simotion for this how it can be done ?
|
10/26/2015 3:37 PM | |
Posts: 95 Rating: (0) |
hi where can I read about this procedure ? |