2/26/2020 3:37 PM | |
Joined: 10/11/2006 Last visit: 4/26/2024 Posts: 5825 Rating: (789)
|
Hello, I think you can use the following FAQ: https://support.industry.siemens.com/cs/ww/en/view/41746959 The alarm which is mentioned there is A01590 (F). You can read out the alarm with your PLC. Hope that helps! |
With best regards, |
|
2/27/2020 2:34 PM | |
Joined: 1/17/2013 Last visit: 4/25/2024 Posts: 1081 Rating: (6) |
Dear Technology Team, It is not much help me from your information. Thank you. How can I control this parameter via PLC ? Best Regards, Vorapob |
Best Regards, |
|
2/27/2020 10:28 PM | |
Joined: 7/7/2010 Last visit: 4/26/2024 Posts: 14637 Rating: (2349) |
I may be wrong, but if you look at the F1-Help for that fault (in Starter or Startdrive), does it show what parameters affect it? Or, if you look in the S120 manual for your CU & motor module(s) for that fault, what parameters are described as affecting that fault? You can use SINA_PARA() from the SIemens DriveLib library to read/write parameters from the PLC to the S120 drive. If the drive is running, some parameters cannot be changed, so verify what is required (preconditions) before attempting to update a value in the drive from the PLC.
|
science guy |
|
2/28/2020 2:32 PM | |
Joined: 1/17/2013 Last visit: 4/25/2024 Posts: 1081 Rating: (6) |
Dear 0_Einstein, Thank you for your information that's good for me. Best Regards, Vorapob |
Best Regards, |
|